Kidde fire detection systems are wired in series. Typical systems use three loops. Troubleshooting is pretty simple.
Probably 95% of the problems are are the engine itself. Isolate both ends of the loops at the pylon disconnects.
I'd guess a 10 to 20 ohm total resistance reading between the ends is pretty normal. High or open readings need to be investigated.
I had a completely open circuit, no visible faults could be seen.
I started pulling on the interconnect wires and.....
The wire wasn't long enough to reterminate,so it was replaced.
As a note, you can use a jumper wire to bypass the wiring (as shown above and below) or one of the complete loops for fault isolation.
The fire detection card can't tell the difference between a jumper or a loop. It just wants to see continuity.....
